    Hello Mathew,

    Fire prevention personnel in North Bay generally issue s & c/o alarm tickets post fire although it is left up to the discretion of the fire prevention officer. Some of our people will only charge by way of part 1 even if it is the owner.

    Joe Gardiner

    Joseph GardinerJoseph Gardiner
    Participant

    Hello Christopher,

    There was a question similar to this one posted a while ago that also might offer some additional information. Below is the link.

    Inspection software?

    Joe, North Bay

    in reply to: Parking in Fire Lanes #10981
    Joseph GardinerJoseph Gardiner
    Participant

    North Bay does the same thing as Richmond Hill .

    Joe

    in reply to: Edwards Heat Detector Recall #10960
    Joseph GardinerJoseph Gardiner
    Participant

    Because of the seriousness of this.

    “Issue: The product may fail to activate, causing users and central monitoring stations to not be alerted to the elevated temperature, in a location, which could lead to the spread of fire.”

    “The product is a mechanical heat detector used in specific indoor applications to detect the presence of an elevated temperature.  It does not detect smoke, nor does it contain an audible notification device as part of the assembly.  This product is professionally installed and used as part of a fire detection system, in places where a smoke alarm would be unsuitable.  In residential settings this product is installed in kitchens, attics and garages for the purpose of property protection, but not life safety.  This detector must be connected to a fire alarm or security panel for monitoring and supervision, as the panel, and not the affected product, drives the connected alarm signals. “

    I have not dealt with this type of situation yet. If I did come across this during an inspection and identified there were detectors falling under this recall I would have the building start a documented “fire watch” until the devices were replaced. Unless, they the owner can prove it does not affect life safety which I believe will be hard to attain. If they can justify that it does not affect life safety, provisions in the fire safety plan to elevate emergency procedures could be amended until the affected devices are replaced. You may also consider updating your fire cad system so that attending fire crews are aware of the situation.

    Hopefully this helps,

    in reply to: Edwards Heat Detector Recall #10957
    Joseph GardinerJoseph Gardiner
    Participant

    Hello Kevin,

    I saw this when it came out and this is how i dealt with it. I looked up our local fire safety suppliers in North Bay and forward the hyperlink to them all advising them of the situation. Most of them were not aware. I also asked the OMFPOA administrator to post it on the OMFPOA website.

    I think sharing it with your local stakeholders is a good way of handling it.

    Joe Gardiner

    North Bay

    in reply to: Fire Department websites #10925
    Joseph GardinerJoseph Gardiner
    Participant

    Good morning John,

    Our website was developed by our city’s IT and the daily upkeep is done by our administrative assistant.

    Hopefully this helps,

    Joe Gardiner

    North Bay

    in reply to: FPPA #10870
    Joseph GardinerJoseph Gardiner
    Participant

    Good morning George,

    Chuck Parsons, the fire chief of Kingsville gave a presentation at the fire college during the 2019 Fire Prevention Seminar regarding a bunch of buildings popping up in his jurisdiction similar to yours and how he and the city dealt with it.

    I think it would be worth you reaching out to him.

    Kingsville fire department  (519) 733-2314.

    Joe Gardiner

    North Bay

    in reply to: home sharing (AIRBNB) #10531
    Joseph GardinerJoseph Gardiner
    Participant

    Hello Nicholas,

    We do not track AIRBNB’s in North Bay. Our office would treat them as if they were a single family dwelling or a dwelling within a multi residential building. I don’t think tracking them in North Bay would serve any major benefit because we have not had any fires here relating to AIRBNB’s. Obvious there are benefits but resources would be better reverted to high priority areas/concerns.

    Hopefully this helps,

    Joe Gardiner

     

    Joseph GardinerJoseph Gardiner
    Participant

    Hello John,

    I am pretty sure our past president Gary Laframboise email: gary.laframboise@oakville.ca might have one that he might share with you. I would send him an email and request a copy.

    Joe Gardiner

    North Bay

    in reply to: Decommissioning of Sprinkler Systems #10358
    Joseph GardinerJoseph Gardiner
    Participant

    Hello Ben,

    Our office would require the owner to get a building permit to decommission the sprinkler system. If they chose not to do that they would have to maintain the system.

    Hope this helps,

    Joe Gardiner

    North Bay

    in reply to: Air Fryers/Deep Fryers #10291
    Joseph GardinerJoseph Gardiner
    Participant

    Hello Mike,

    Here are my thoughts with the information you have provided. I would first check that the building department knows this restaurant exist just in case the change of use has not been done. The change of use will almost always sort your problem out. I would then do the following if the change of use has been done.

    ·       Ensure the current situation applies to the Ontario Fire Code – under the application of Part 2 OFC and the articles I have provided below.

    ·       If the situation meets OFC requirements NFPA 2011-96 is applicable.

    ·       NFPA 96 states that All listed appliances shall be installed in accordance with the terms of their listings and the manufacturer’s instructions.

    ·       If you look up the manufacturer’s instructions you will find a clause in there somewhere that states “this device is not intended for commercial use”. If you can find that, it is a done deal.

    ·       If it doesn’t say that they will have to protect the device as per NFPA 96 2.6.1.12. & 2.6.1.13 which will more than likely correct the situation.

    Hopefully this helps you out. See below.

    Joe Gardiner, North Bay Fire,

    O. Reg. 213/07: FIRE CODE

    Exhaust and fire protection systems in cooking operations

    2.6.1.12. (1) A cooking operation producing smoke or grease-laden vapours shall be provided with an exhaust system and fire protection system in accordance with NFPA 96, “Standard for Ventilation Control and Fire Protection of Commercial Cooking Operations”.

    (2) Despite Sentence (1), an existing exhaust or fire protection system may be approved.

    (3) Sentence (1) does not apply to

    (a) an individual suite of residential occupancy, or

    (b) a cooking operation producing insignificant amounts of smoke or grease-laden vapours that are controlled by other approved measures.

    (4) In a hotel establishment regulated by Section 9.9, a cooking operation that meets the requirements of Article 9.9.2.19. is deemed to be in compliance with Sentence (1).

    Maintenance of exhaust and fire protection systems

    2.6.1.13. Exhaust and fire protection systems required under Article 2.6.1.12. shall be maintained in accordance with NFPA 96, “Standard for Ventilation Control and Fire Protection of Commercial Cooking Operations”.

    2.6.1.14. (1) Instructions for manually operating the fire protection systems required under Article 2.6.1.12. shall be posted conspicuously in the kitchen.

    (2) The instructions required in Sentence (1) shall be included in the fire safety plan where such a plan is required.

    2011- NFPA 96 Chapter 12 Minimum Safety Requirements for Cooking Equipment
    12.1.2 Installation.
    12.1.2.1 All listed appliances shall be installed in accordance
    with the terms of their listings and the manufacturer’s instructions.

    in reply to: Micro Breweries #10267
    Joseph GardinerJoseph Gardiner
    Participant

    Hello Randy,

    Sorry for the late response. The occupancy is being changed from an E to a F2 or F3 and will need a “change of use” permit which will require the owner to more than likely get an architect to look at the process and determine OBC requirements. This will sort out all fire separation/equipment requirements.

    Let me know if this helps?

    Joe Gardiner

    North Bay Fire

     

    in reply to: Smoke alarm expiry #9893
    Joseph GardinerJoseph Gardiner
    Participant

    Hello Jon,

    I find charging just one person for an expired smoke alarm/carbon monoxide alarm a very good way of spreading the news. I don’t suspect it is very creative but it is very effective. One charged person will reach out to hundreds of people.

    Joe Gardiner

    North Bay Fire

    in reply to: Defective revice reporting? #9821
    Joseph GardinerJoseph Gardiner
    Participant

    Good morning Jon,

    I don’t know if there is a different reporting procedure.

    I am interested to know who the testing agency was? CAN/UL? You may want to notify them and also the Electrical Safety Authority.

    I have had a couple of instances now of owners buying CO alarms online not tested by any registered testing agency like CAN/UL. Obviously I had them remove the units immediately and purchase real ones.

    Thanks Jon,

    Joe Gardiner, North Bay

    in reply to: Inspection Orders with Building Permits #9798
    Joseph GardinerJoseph Gardiner
    Participant

    Hello Jon,

    • Order is issued to create a service room to separate equipment from the remainder of the floor area.
    • Drawings submitted to Bldg Dept and Permit issued
    • Who does the inspection? Fire or Bldg?I’m thinking Bldg inspects, Reply – Our/Fire department does all followup visits. 
    • Bldg Permit closed, Reply – After the fire department does the final inspections. 
    • Report back to FD (by either the Owner or Bldg) Reply – Fire does final inspection. 
    • Fire Order completed.