  • Andrew McMillanAndrew McMillan
    Participant

    Hi Matt,

    From my understanding, ATSM84 is equivalent to CAN/ULC-S102. It might be best to have them present this as an alternative solution. The big issue that I have found is that some of the vinyl films exceed the flame spread rating allowed.

    Feel free to reach out

    amcmillan@stclairfire.ca

    in reply to: Locking doors in a group home #13977
    Andrew McMillanAndrew McMillan
    Participant

    We dealt with a group home here in a similar situation and have another one on the go right now. Both are B occupancies. The one requested to put a lock on the bedroom door and advised us that staff would unlock the door in the event of an emergency. We didn’t allow it. We did take the time to educate the building owner on the potential risks. Maglocks were eventually installed in the building. A building permit was obtained for this installation. They were required to met OBC requirements which, required a fire alarm system and emergency lighting to be installed. The fire safety plan was also updated to reflect the change.

    Andrew McMillan
    amcmillan@stclairfire.ca