A message from our Symposium Keynote speaker Peter Katz Peter Katz is a Juno Award- and Canadian Screen Award-nominated singer-songwriter who has spent the past 20 years touring internationally. He has been described by many of his fans and speaking clients as โ€œa thunderbolt for the soulโ€. A gifted storyteller fluent in English and French,

Read More ยป

Membership Renewal Reminder

OMFPOA Memberships expire at the end of each calendar year. As we have had ongoing website construction and upgrades being completed we have not removed any accounts that have yet to pay for 2023. Our membership continues to increase and we hope to have you as part of our association. This post is to serve

Read More ยป

HOME Forums Reply To: Plastic Apex Piping – 9.5 and 9.8 Occupancies

#1748
Charles TurpinCharles Turpin
Participant

I would refer back to NFPA 13R Standard for installation of sprinklers systems in residential occupancies up to and including four stories in height 2010 edition
Chapter 5 System components – section 5.2 Above ground Piping And Equipment that refers to the table 5.2.1 or accordance to 5.2.2
Table 5.2.1 speaks to the pipe being made of a metal. Where 5.2.1.3 When nonmetallic pipe is used, the pipe shall be designed to withstand a working pressure of not less than 175 psi (12.1 bar) at 120F (49C)
and 5.2.2 Types of pipe other than those specified in Table 5.2.1 shall be permitted to be used where listed for sprinkler system use.
And read on in section 5.2.2
I short if the owner could prove that the pipe meets the NFPA criteria then yes