December 24, 2019 at 7:47 am #10999
Julien Boisvenue
ParticipantGood morning! Just got my user ID and password for the OMFPOA, so looking forward to accessing this site for resources and knowledge. I’m looking for any information or suggestions for intumescent paint. I have recently served an inspection order and this would be an possible option.
Thanks!
-
December 24, 2019 at 9:52 am #11000
Andrew Dickson
ParticipantJulien,
An owner we served an inspection order had to treat some wood as well as some carpet. The 2 products they used in their application were Flame Control and Inspecta-Shield.
Hope it helps.
Andrew Dickson
-
December 27, 2019 at 9:04 am #11001
John Wilson
ParticipantWelcome to the site Julien.
The biggest thing I look for with intumescent paint is that it has to be tested to CAN/ULC S101 for the given situation at hand. I’ve had it proposed to me for several different situations, some I accepted, some I didn’t. People tend to think it’s a magic solution (can’t we just paint everything?) and often figure out that drywall is cheaper once they see the price of the intumescent paint.
For example: Original door in a historic church? Sure, I’ll accept that. Wood paneled stairwell in an apartment building? Nope, give me drywall.
I have the Owner provide me with all the supporting documents for review before and upon completion require a signed letter of acknowledgement on letterhead from the painting contractor that it was applied as per manufacture’s instructions.
You may also want to check with your Building Department for their opinion as creating new separations technically requires a building permit.
-
-