March 31, 2020 at 1:59 pm #12598
Vince Tripp
ModeratorHello all, I hope you are all doing well during this pandemic.
York Region is looking at using some city facilities as potential overflow areas for non-critical patients should the need arise. Potentially using arenas/community centers or libraries as Field Hospitals. Has anyone run into this yet at their location? What measures would you put into place for fire safety? Fire watch for sure. We are thinking about using the OFM Technical guideline “Use of Schools for Sleeping Accommodations” as a basis.
Thanks
-
April 1, 2020 at 9:51 am #12601
Scott Hardwick
ParticipantHello Vince,ย ย I would use that guideline too.ย Ensure you are in the planning stage of this discussion.ย Sometimes locations that don’t have a fire alarm system is offered up, only to be rejected by the Fire Department later.
Scott Hardwick, FPO
Brantford Fire Department
-
April 1, 2020 at 10:47 am #12602
Vince Tripp
ModeratorThanks Scott
-
April 3, 2020 at 4:24 pm #12623
Shannon Suzuki
ParticipantIf all can self-evacuate, here are some ideas:
– all main doors to suites and stairwells have a functioning self-closing device and can latch
– smoke alarms in sleeping rooms. CO alarm alarms as per 2.16 of the Code (assume residential)
– fire safety plan updated, reviewed and approved.
– ensure that check/test/inspect on all existing fire and lift safety equipment (fire alarm system, sprinkler system, fire extinguishers, emergency lights, generator, fire pump etc) is current and compliant with the Fire Code.
S
-
April 15, 2020 at 9:20 am #12659
Nicholas MacGillivray
Participantnew communique 2020-09
-
April 15, 2020 at 3:39 pm #12664
John Wilson
ParticipantGot a link to that Nick? 2020-07 is the newest on the OFMEM page
-