  Delta Hotels London Armouries has created a website to enable Symposium attendees to register at the discounted rate. Follow the instructions below to book . Further information on the Symposium and registration forms can be found here. Book your group rate for OMFPOA 2023 Symposium Thank you for considering to stay at the Delta

Read More »

HOME Forums Forums Fire Code & Enforcement Apartment suites with self closing doors

Viewing 3 reply threads
  • Author
    Posts
    • #10972
      Chris MatthewsChris Matthews
      Participant

      In apartments with self closing doors at each suite, must the doors remain closed except to enter or exit the suite or are occupants allowed to keep doors open to circulate air ? Also, are the door closiers required to be inspected by a building staff member each month?

    • #10973

      the door is a requirement for the fire separation, so yes it must remain closed. you can issue a ticket for it also

      14.
      Closure in fire separation wedged open
      Article 2.2.3.3. of Division B
      $295.00

      the self closing feature is also part of the door , which is a fire separation, so yes it has to be inspected as part of the separations

    • #10974
      John WilsonJohn Wilson
      Participant

      Also see 2.2.3.4. (1) a door in a fire separation shall be kept closed when not in use

      (2) A door in a fire separation shall be checked as frequently as necessary to ensure that the door remains closed.

      (3) Sentences (1) and (2) do not apply to

      (a) a door designed to close automatically in the event of a fire emergency, or

      (b) a door for which an approved fire safety plan contains provisions for closing in the event of a fire emergency.

      (4) A door in a fire separation shall be inspected monthly.

       

      So even a door in a fire separation without a self-closing device must be kept closed unless it meets Sentence (3) like if there was a magnetic hold-open (happens often) or part of the fire safety plan (which I only approve under limited circumstances and your’s isn’t one of them)

    • #10983
      Chris MatthewsChris Matthews
      Participant

      Okay, thank you for helping me clear that up.