  Delta Hotels London Armouries has created a website to enable Symposium attendees to register at the discounted rate. Follow the instructions below to book . Further information on the Symposium and registration forms can be found here. Book your group rate for OMFPOA 2023 Symposium Thank you for considering to stay at the Delta

Read More »

HOME Forums Forums Fire Code & Enforcement Combustible sprinkler piping, blazemaster, orange pipe Reply To: Combustible sprinkler piping, blazemaster, orange pipe

#9697
John WilsonJohn Wilson
Participant

Contractor and/or manufacture won’t trump the OBC. As Charles quoted  “Where sprinklers are not required, and when approved by the authority having jurisdiction, it is acceptable to install BlazeMaster products exposed in these areas.”  But before you even get to the OBC 3.2.5.14.(5)  that he mentioned, 3.2.5.14.(1) ‘Combustible sprinkler piping shall be used only for wet systems in residential occupancies and other light hazard occupancies.’ must be satisfied.  There are many factors in play to determine if it needs to be protected:

New construction or existing building?

Does it meet that 3.2.5.14.(1) clause?

If it’s new, what’s the OBC building classification (3.2.2.x.) ?

Are they installing sprinklers as an Alternative Measure to something or are they installing because it is required to be sprinklered?

Building Inspector is likely considering many more factors than the contractor.