  Delta Hotels London Armouries has created a website to enable Symposium attendees to register at the discounted rate. Follow the instructions below to book . Further information on the Symposium and registration forms can be found here. Book your group rate for OMFPOA 2023 Symposium Thank you for considering to stay at the Delta

Read More »

HOME Forums Forums General Wet vs Dry sprinkler systems Reply To: Wet vs Dry sprinkler systems

#9687
Tyler FournierTyler Fournier
Participant

Jon,

There is nothing in the Fire Code or Building Code that I can find that indicates that you cannot use a dry system in a heated area. The Building codes makes reference to automatic sprinklers systems shall be designed, constructed, installed and tested in conformance with NFPA 13 (Sentence 3.2.5.13.(1)).

NFPA 13 (see 7.2 Dry Systems) states that dry pipe systems should only be installed where heat is not adequate to prevent freezing of water. So, in my opinion, as long as you can meet the dry pipe system water delivery time based on the hazard, a dry system is adequate. It would be a recommendation for the building owner and/or tenant to convert the dry system to a wet system.