  Delta Hotels London Armouries has created a website to enable Symposium attendees to register at the discounted rate. Follow the instructions below to book . Further information on the Symposium and registration forms can be found here. Book your group rate for OMFPOA 2023 Symposium Thank you for considering to stay at the Delta

Read More »

HOME Forums Forums Fire Code & Enforcement 9.5 Exterior Stairs vs Fire Escape Reply To: 9.5 Exterior Stairs vs Fire Escape

#12652
George MacrisGeorge Macris
Participant

Hi Jon,

If the exterior stair serves a required exit then these stairs are considered  a “fire escape” and need to apply all the requirements as mentioned in 9.5.3.7.

If the exterior stairs does not serve a required exit then you don’t apply any of the requirements in 9.5.3.7. That all you have to worry about.

The requirement for protection of openings on the building wall is to prevent a fire from breaking through the openings and preventing occupants from exiting via the fire escape. If this is not a fire escape because it does not serve a required exit there is no need for protection according to the code because it’s not a required exit, technically it can be blocked off.

I’m not sure why Rob above is asking you to obtain an engineer’s report for the exterior wall. Why would a wall have a fire resistance rating and furthermore this has nothing to do with the subject matter, it’s not applicable. We don’t even have the right to ask for an engineers report, what reference you are going to use? Also a fire escape is permitted to be installed under 9.5.3.7.;we are not enforcing the OBC on a new building, that’s the Building Department.

Keep safe,

GM