  Delta Hotels London Armouries has created a website to enable Symposium attendees to register at the discounted rate. Follow the instructions below to book . Further information on the Symposium and registration forms can be found here. Book your group rate for OMFPOA 2023 Symposium Thank you for considering to stay at the Delta

Read More ยป

HOME Forums Forums Fire Code & Enforcement Clearance around and in front of an electrical panel Reply To: Clearance around and in front of an electrical panel

#11357
Al BastienAl Bastien
Participant

Hi Julien.

Hope this helps:

The Ontario Electrical Code:

Rule 2-308 Working space around electrical equipment
(1) A minimum working space of 1 m with secure footing shall be provided and maintained about electrical
equipment such as switchboards, panelboards, control panels, and motor control centres that are enclosed
in metal, except that working space is not required behind such equipment where there are no renewable
parts such as fuses or switches on the back and where all connections are accessible from locations other
than the back.

(2) The space referred to in Subrule (1) shall be in addition to the space required for the operation of drawout-
type equipment in either the connected, test, or fully disconnected position and shall be sufficient for
the opening of enclosure doors and hinged panels to at least 90ยฐ.

(3) Working space with secure footing not less than that specified in Table 56 shall be provided and maintained
around electrical equipment such as switchboards, control panels, and motor control centres having
exposed live parts.

(4) The minimum headroom of working spaces around switchboards or motor control centres where bare live
parts are exposed at any time shall be 2.2 m.